We're proposing a deployment of carrier backhaul chassis that only come in a -48VDC option. The chassis has side A and B input and can alert power failure on either side.

That being said I have next to no experience with rectifiers, but I sort of know what I want.

My director originally spec'd the following Newmar shelf:

http://www.newmartelecom.com/Unity-Rectifier-System/Unity-Rectifier-System.html

I like that it supports a third module for active failover, but the modules connect in parallel to the fuse block, so side A and B output are not tied to separate modules. Therefore if a module fails in the field we have no way of knowing without putting eyes on the install. Also I'd have to supply a separate UPS for backup which I'd prefer to have an all-in-one solution and not rely on another unit.

Having separate side A and B output power isn't as important as a good rectifier, built-in UPS in a 2U form factor and bypass option for swapping batteries. I'll consider all options.

Here's an example of a shelf I'm looking at. The downside is there's only one set of outputs on the rear:

http://www.newmartelecom.com/IPS/IPS.html

Any help from those with experience would be greatly appreciated.

Edit: Input power is 120VAC, Output amps up to ~5
 
Last edited:
I prefer Eaton's systems due to their high modularity and stellar service options.

You didn't really indicate how much amperage you are shooting for, but http://dcpower.eaton.com/3g/EPS2-Series.asp is similar to the Newmar gear you've shown here. Note the the matching battery backup modules for said unit.

Edit - You need 5 amps, so hardly much at all. So the above shelf with two of these http://dcpower.eaton.com/3G/EPR48-info.asp You really only need one, but throwing in two gives you the redundancy at least.

The Newmar setup will end up being cheaper, but lacks the remote management / monitoring capabilities, and efficiency that Eaton systems usually provide.

You won't have *true* redundancy with either self contained system on your actual gear. That being said either setup from either company has built in redundancy with the actual rectifier modules so I wouldn't worry about it.
 
Last edited:
Thanks for the Eaton recommendation. I'll take a look at their offerings.

I'm going to evaluate our space requirements to see if we can squeeze in an extra rack unit or two.
 
At our COs we use mostly Cordex/Argus system, think it's made by Alpha.

Though I'd be curious to see what else is recommended in this thread, as I can't seem to find anywhere online to buy -48vdc rectifier systems, I'd like a small chassis at home, with like 3kw capacity or so. No idea how it would even cost. No sites seems to want to show prices and offer a add to cart option.
 