• Some users have recently had their accounts hijacked. It seems that the now defunct EVGA forums might have compromised your password there and seems many are using the same PW here. We would suggest you UPDATE YOUR PASSWORD and TURN ON 2FA for your account here to further secure it. None of the compromised accounts had 2FA turned on.
    Once you have enabled 2FA, your account will be updated soon to show a badge, letting other members know that you use 2FA to protect your account. This should be beneficial for everyone that uses FSFT.

Need: Modular with active PFC

OuTLaWzSm

Limp Gawd
Joined
Sep 26, 2004
Messages
204
title says it all. in the 500 watt range, SLI capable. also i want to sleeve it with UV cables sleeves any recomendations, it would be really nice if i didn't have to remove the connectors and then put it on. if i could just slide the cable sleeve over the connector.

thanks,
outlawzsm
 
it helps a little in the way of heat in the US.

Most would recommend the Enermax Liberty
 
Steeeeve said:
it helps a little in the way of heat in the US.
Actually, PSUs equipped with Active PFC tend to run a little hotter and less efficient compared to units without the circuit.
 
they also do far far better on a UPS, I wont buy a PSU without PFC these days

http://powerelectronics.com/mag/power_power_supply_system/index.html

UPS Nonlinear Loads

Most end users are oblivious to the problems encountered when an online UPS interacts with nonlinear load, such as a switchmode power supply. Fig. 3, on page 42, illustrates the interface between an online UPS and a switchmode power supply. The switchmode supply within the host system consumes its current in high amplitude pulses, and as a result overloads the UPS, distorts its output and degrades in performance. This isn't the case if the SMPS has power factor correction (PFC); and in the United States most SMPS don't have PFC.

Repeated measurements under practical conditions show that in non-PFC SMPS, the current peak to rms ratio reaches a crest factor in the range of 2.5 to 3.5. This high crest factor imposes a difficult load for the UPS.

Manufacturers specify UPS capacity in volt-amperes, and set the UPS current limit with resistive loading. This affects the user in two ways: first, the actual power (in watts) that the online UPS can deliver is 75% to 80% of its VA rating. Second, the UPS cannot support a nonlinear load like a SMPS to full power capacity. In fact, it can support an SMPS only rated to 30% to 40% of its capacity. A 1kVA online UPS will only be suitable for backing up a system energized by a 300W to 400W (non-PFC) switchmode power supply. Attempts to draw higher power by the SMPS will severely distort the output of the UPS and may result in shutdown. Some UPSs support nonlinear loads to various degrees, but the above rule is safe to use as a guideline.

The whole idea of generating a high-purity sinewave within the UPS, and then rectifying it within the SMPS is wasteful. A UPS may be deployed to run non-electronic loads, such as lights or motors. However, this is a minor portion of the market for online UPS. Many applications back up computers and telecom devices, as well as instrumentation systems used for critical applications. In all of these applications, the immediate load for the UPS is the SMPS within the systems. Peak current and inrush current are associated with this load at startup. This current of 40A to 80A per SMPS will cause the UPS to shutdown due to overloading, or the UPS must transfer the load to utility to draw its inrush.
 
_Korruption_ said:
Actually, PSUs equipped with Active PFC tend to run a little hotter and less efficient compared to units without the circuit.

I didn't know that...where did you hear that?
 
I have the Enermax lib 620Watt model and shes working great for me
 
k i've decided on the antec neoHE 550, the enermax has to many SATA which i think is stupid because i only need one.

now for the sleeving would you recommend the techflex UV or Vantec UV kits? also anyone using the AC Ryan connectx?
 
Back
Top