how many amps would a PC,TV,ect use?

SniperXx

2[H]4U
2FA
Joined
Jun 7, 2001
Messages
3,478
I have a 100 foot extension cord that I am wanting to run to a building next to my house which will have a Athlon 64,19" CRT,4.1 speakers,27" TV,Xbox,DVD player,ect hooked to it. The cable is 10amp/125v cord. Would 10amps be enough to power all this at once if need to be? I don't want to cord getting hot and possibly causing a fire.
 
Extension cords are not meant for permanent installation, especially with an outdoor run and at that length. If this is going to be a permantent installation then you really should use conduit and proper wire. If the wire is going to be elevated then you can probably get by without the conduit so long as you have the proper wire. If it is going to be on the ground/below ground then I'd recommend conduit to protect the wire from critters and the weather. You could probably get by with an extension cord, but it is definitely against code(if codes apply to you), and for good reason. Though if this is just going to be a temporary thing then you should be fine.

As a side note, my parents just moved to a house out in the country. The previous owners had buried an extension cord in the yard to power the pool equipment. It worked, but I would never do anything like that myself.
 
Well watts are amps * volts. The cord is theoretically rated for 1250 watts. I think if you add all that stuff up, you're going to exceed 1250 watts. Given that, and the fact that an extension cord (especially at that length and outdoors) isn't really meant to power things like that, I would say it's not the best idea.

The other consideration is the load on the circuit this is going to be plugged into. What else is on that circuit? Is it a 15A or 20A circuit?
 
nomar said:
Well watts are amps * volts. The cord is theoretically rated for 1250 watts.

Of course, Ohm's Law only applies to non-inductive, DC loads. A computer power supply most certainly isn't a non-inductive load.

Like jpknm says, if the lead is going to be there for any length of time, you probably want to find a solution that's both safe and up to code.
 