I've read that active PFC can help by allowing a less expensive UPS since most UPSs are priced based on VA rating. However, they also have a maximum wattage rating. I've read that most companies specify the maximum wattage rating as 60% of the VA rating. My question is: do they do this because most PSUs are inefficient and they want to be conservative, or is there really some sort of hardwired limit set to 60% of the VA rating?
For example, if I went with an Enhance ENP-5150GH (http://www.80plus.org/manu/psu/documents/EnhanceElectronics_ENP-5150GH_80PLUS_Report.pdf), it draws 603VA apparent power at maximum load. Say I went and got a 650VA unit from APC. It is speced at 390W. According to that 80plus.org document, the Enhance will pull 486W real power due to its high efficiency and active power factor correction. Does that mean the APC unit is out, or is the 390W designation just an extra number they throw in so the average consumer doesn't get confused and try to run to much on there with his crappy, inefficient power supply?
For example, if I went with an Enhance ENP-5150GH (http://www.80plus.org/manu/psu/documents/EnhanceElectronics_ENP-5150GH_80PLUS_Report.pdf), it draws 603VA apparent power at maximum load. Say I went and got a 650VA unit from APC. It is speced at 390W. According to that 80plus.org document, the Enhance will pull 486W real power due to its high efficiency and active power factor correction. Does that mean the APC unit is out, or is the 390W designation just an extra number they throw in so the average consumer doesn't get confused and try to run to much on there with his crappy, inefficient power supply?