Hi,
Was tripping the breaker every now and then while encoding video or gaming on a 1200 watt psu and 5820K cpu. Is it safe to run extension cord to dry outlet where the breaker is rated at 50A?? At least for an hour at a time..
Thanks
You shouldn't be close to tripping the breaker. 15a*120v= 1800watts. I've run breakers at 1500 watts for months with no incident.
You have an extension cord plugged into a dryer outlet? That's not safe at all, especially if it's the older 3-prong variety.
Also, 1200w load = 1500w from the wall (assuming 80% efficiency). Add in 75-150w per monitor, one or more 40-60w light bulbs, 20-100w speakers... it's gets easy to overload a 15a breaker.
I guess but the dryer plug looks like a standard 3 prong plug. Rated at 50A.
Power went out in both rooms?Then last week when it happened again I remember I had my second machine running in the spare second bedroom at the same time as my primary gaming rig both encoding video, and power went out in both rooms.
That's what I thought he meant until he said "standard", whichI took to mean was a NEMA 5-15R. Dryers typically use a NEMA 14-30R or the older NEMA 10-30R (which are 30amp and won't fit a 50 amp plug).He's referring to an older 230 VAC three prong appliance plug. Nowadays, NEC dictates a four prong for dryers and other appliances with heavy power draw.
.
if it is only as thick as the psu cord, that is probably not thick enough(lower gauge). you could run a risk of the cord overheating and starting a fire. the cord has to be rated for a minimum of 20Aumm, if I remember right 1800w is the limit for 15A/120V. so yeah if you total everything up that is on that same breaker and it exceeds 1800w, poof it blows. next time it blows take note of everything that turns off, make a total. and running your tower on an extension is ok AS LONG as it is a low enough gauge(thick, high amp).
if it is only as thick as the psu cord, that is probably not thick enough(lower gauge). you could run a risk of the cord overheating and starting a fire. the cord has to be rated for a minimum of 20A
I was just going by what the system is drawing. yes if there were some strange catastrophic failure it could potentially surge the full 50a. and I'm still not sure how he is plugging in a regular 3 prong extension cord into a massive dryer socket. maybe he has it in the washer socket, mine is a 20a 3 prong...If he's plugging into a 50a outlet, it needs to be a minimum rating of 50amps.
And yes it's still dangerous. Until you can verify that the outlet you're using is properly wired and protected, you may be plugging a cord designed for 120v applications into a 240v supply. Most modern PC power supplies are rated for 100-250v, so they can handle it, However, if something were to short out, up to 50a could be forced through a 15-20a cord, outlet, and possibly even the interior wiring. Bad things will happen then.
An elevator doesn't mean your place has modern electrical wiring.You guys are right I'm not sure about the specifics about the electrical coming in to my apartment. I live in the United States in Massachusetts in a fairly modern style complex. The place even has an elevator.
Hi,
This is what the dryer plug looks like:
And I was wrong about the Amp rating. Its rated at 30 Amps according to the map in the breaker box legend.
Also since I believe that was tripping the 15 amp breaker was high peaks of voltage and not necessarily sustained
draw of amps so I should be ok with a 16 amp rated extension cord for light use while gaming right?
Considering if my system pulls max 800 watts while gaming using two gpus that would be like 6.6 amps
and even less if I'm just using the cpu to compress videos?
Heres what the breaker box looks like:
The breaker may be 30amps but the receptical is definitely a 20amp part.Well according to breaker legend its 30 amp and thats how it was when I started renting the place.
Better than 15 amps in my opinion.
Thanks
Hi,
This is what the dryer plug looks like:
<img removed>
And I was wrong about the Amp rating. Its rated at 30 Amps according to the map in the breaker box legend.
high peaks of voltage come from the power grid and are generally not going to trip a breaker (but will fry electronics). So assuming you have a clean supply of electricity and there there were no storms around, the voltage will stay constant regardless of how many things you plug in (that's not entirely correct, but let's go with it). So it was TOTAL amp draw from ALL the devices plugged into that branch that flipped your breaker.Also since I believe that was tripping the 15 amp breaker was high peaks of voltage and not necessarily sustained
draw of amps so I should be ok with a 16 amp rated extension cord for light use while gaming right?
Considering if my system pulls max 800 watts while gaming using two gpus that would be like 6.6 amps
and even less if I'm just using the cpu to compress videos?
Heres what the breaker box looks like:
<image snipped>
I'm sure its the dryer that was plugged into that outlet. The plug for the washer is twice as big and much different in stlye. You guys notice that the wiring in regards to the breaker isn't correct?
I get it was probably the total amp draw from two computers and a couple modem routers plus a few lights that tripped it, but the peaks I was referring to was random sways of the psu pulling power. It never stays at a constant level. Has highs and lows.
Attached a couple more photos.
Thanks
Not sure why they're horizontal.
haha, I didn't' even notice.I guess I'll have to switch the breakers off to test where they're going. Probably mislabeled as the electrician probably couldn't even spell. 'WashingMachine' is labeled 'WashingtonMachine'!
Maybe he was trying to make a political statement...
Hmmm...
Thanks
I was looking at 20+A extension cords and they all had the male and female ends like this " - | " so you couldn't use normal 15A plugs on them.The good news is that 20-amp outlets are usually dedicated, meaning there are no other outlets, lights, etc. on the same circuit. You can safely use this outlet but if you do, go to Lowe's or Home Depot and pick up a heavy gauge extension cord. A single cord long enough for the task, not multiple short ones. Make sure it's rated for 20+ amps.
that is deff a washer outlet. but you are wrong. anything 120v can plug into it just fine and it will work just fine. the socket is simply able to support up to 20 amps. trust me, ive installed dozens of them into every big orange hardware store in my province even though they didn't really need them(according to the journeyman electrician working with me). everything connected was standard 15a three prong but they requested 20a. still working great years later!Like was mentioned above, that's a 120v-20a outlet. It will not be usable by most electric dryers. Gas dryers and maybe a "space saver" dryer. Are you sure that's not for the washer instead?
like I said, washer outlet. soon as he said he used a normal extension cord. It would take someone reeaaal special to jam one into the dryer sockets!The 20a single pole breaker labeled Washing Machine (12) matches what the outlet you showed us should be wired to
skip amazon and run to your local. shit Walmart even. and yeah that cord is fine and you pc load is well below it rating. get one that is appropriate length as you don't want a bunch coiled up.as I found some on Amazon that can accept both types